HO DOVUTO RICARICARE TUTTI I DATI MACCHINA PERSI E L'APPARECCHIATURA SI E' AVVIATA.
ANCHE IL PLC E' IN RUN, CON UNA SERIE DI ERRORI RELATIVI A DIGITAL INPUT ASSENTI.
NELLA CONFIGURAZIONE, DOPO LA CPU PLC (6FX1138) SONO INSTALLATE N° 4 SCHEDE N71(6FX1125) (DIGITAL INPUT), 2 N72( 6FX1122) (DIGITAL OUTPUT) .
LE HO TESTATE CON UN MODULINO EUROGI A 32 BIT CON INGRESSI FORZATI A 1 E UN CAVO FLAT DI COLLEGAMENTO SULLE PORTE X111 E X121 DI OGUNA DELLE N71.
LE PRIME DUE IN POSIZIONE C12 E C13 SONO PERFETTAMENTE FUNZIONANTI PERCHE' LEGGO SULLO SCHERMO DEL PANNELLO OPERATORE TUTTI I BIT A 1.
C12 X111 DAL BIT E0.0 AL BIT E3.7 (PASSANO TUTTI A UNO);
C12 X121 DAL BIT E4.0 AL BIT E7.7(PASSANO TUTTI A UNO);
C13 X111 DAL BIT E8.0 AL BIT E11.7(PASSANO TUTTI A UNO);
C13 X121 DAL BIT E12.0 AL BIT E15.7(PASSANO TUTTI A UNO).
LA SUCCESSIVA N71 COLLOCATA IN C14 NON RICEVE ALCUN INGRESSO SU ENTRAMBE LE PORTE:
X111 DAL BIT E16.0 AL BIT E19.7 (RIMANGONO TUTTI A ZERO);
X121 DAL BIT E20.0 AL BIT E23.7 (RIMANGONO TUTTI A ZERO).
IDEM SULLA SCHEDA N71 POSTA IN C15.
INVERTENDO LA POSIZIONE DELLE SCHEDE (RISPETTANDONE LA PERSONALIZZAZIONE) IL GUASTO RIMANE SEMPRE SUGLI INGRESSI DA E16.0 A E23.7(POSIZIONE DELLA SCHEDA N71 IN C15).
IL BUS POSTERIORE DEL RACK E' STATO SOSTITUITO CON ALTRO UGUALE MA NON NUOVO, DANDO LO STESSO PROBLEMA.
I DATI TEA1 (DATI MACCHINA CN) E TEA2 (DATI MACCHINA PLC) SONO QUELLI ORIGINALI RICARICATI PIU' VOLTE IN PASSATO.
NON RIESCO AD "ATTIVARE " GLI INGRESSI MANCANTI.
GRAZIE A CHI POTRA' AIUTARMI.